I'm putting together a bank of 3 batteries, connected in parallel for use in a solar PV system. The primary load will come from a 1000W inverter (2000w surge). The inverter manual recommends using a 3ft. run of 25mm^2 cable to connect to the batteries.
Is the size of the interconnects dependent on the maximum load the batteries can be expected to deliver or is there another factor which needs to be considered?
Edit: The battery bank consists of 3x 12V AGM batteries. The inverter draws 1000W @ 13V under normal operation but will pull 2000W @ 13V for brief periods when necessary. This means I should use wire that can carry 154 amps (2000W / 13V = 153.8 amps) from the battery bank to the inverter. Should the size of wires used to connect the batteries together be calculated using the same amount of current (154 amps, which is the largest load that will be connected to them)?